If kilowatts are known, which expression gives current in a three-phase system?

Prepare for the SEPTA Electrician Test with flashcards and multiple choice questions. Each question offers hints and explanations to boost your preparation. Be exam ready!

Multiple Choice

If kilowatts are known, which expression gives current in a three-phase system?

Explanation:
In a three-phase system, real power relates to current by P = √3 × V_L × I × PF. To find the current when given power in kilowatts, convert P to watts (P = KW × 1000) and solve for current: I = P / (√3 × V_L × PF). This becomes I = KW × 1000 / (Volts × PF × 1.73), using 1.73 as an approximation for √3. The denominator must include Volts, PF, and the √3 factor because each plays a role in determining how much current is needed to deliver the real power: voltage provides the driving potential, PF accounts for how much of that power is actually doing useful work, and √3 arises from the relationship between line voltage and line current in a three-phase system. For example, with 100 kW, 480 V, and PF of 0.9, I ≈ 1000000 / (480 × 0.9 × 1.73) ≈ 134 A.

In a three-phase system, real power relates to current by P = √3 × V_L × I × PF. To find the current when given power in kilowatts, convert P to watts (P = KW × 1000) and solve for current: I = P / (√3 × V_L × PF). This becomes I = KW × 1000 / (Volts × PF × 1.73), using 1.73 as an approximation for √3. The denominator must include Volts, PF, and the √3 factor because each plays a role in determining how much current is needed to deliver the real power: voltage provides the driving potential, PF accounts for how much of that power is actually doing useful work, and √3 arises from the relationship between line voltage and line current in a three-phase system. For example, with 100 kW, 480 V, and PF of 0.9, I ≈ 1000000 / (480 × 0.9 × 1.73) ≈ 134 A.

Subscribe

Get the latest from Passetra

You can unsubscribe at any time. Read our privacy policy